During a verification, when a ground fault is introduced on a Data Communication Link (DCL), what is the required result?

The standard specifies that for DCLA (Data Communication Link) wiring, a ground fault must be introduced to ensure it does not interfere with system operation o

Start free practice for ASTTBC RFPT — Fire Alarm Systems (AL)

30 questions · no signup required · 40 free questions per day

Start Practice →

Question: During a verification, when a ground fault is introduced on a Data Communication Link (DCL), what is the required result?

Answer options:

  • The system must remain in normal state without trouble
  • The system must automatically bypass the shorted section ✅ A trouble signal must be generated at the control unit
  • The system must immediately enter an alarm state

Correct answer: A trouble signal must be generated at the control unit

Explanation: The standard specifies that for DCLA (Data Communication Link) wiring, a ground fault must be introduced to ensure it does not interfere with system operation or that it reports as a trouble.