ASTTBC RFPT — Fire Alarm Systems (AL) · Question

For a Class B notification appliance circuit, the end-of-line supervisor device must be located:

CAN/ULC-S536 (Testing) and S524 (Installation) specify that if an End-of-Line (EOL) resistor is used, it must be located after the last device on a Class B circ

Start free practice for ASTTBC RFPT — Fire Alarm Systems (AL)

30 questions · no signup required · 40 free questions per day

Start Practice →

Question: For a Class B notification appliance circuit, the end-of-line supervisor device must be located:

Answer options: ✅ At the last device on the circuit

  • Inside the fire alarm control unit cabinet
  • In a junction box exactly halfway through the circuit
  • At the 'Designated Entrance' remote annunciator

Correct answer: At the last device on the circuit

Explanation: CAN/ULC-S536 (Testing) and S524 (Installation) specify that if an End-of-Line (EOL) resistor is used, it must be located after the last device on a Class B circuit. Putting it in the panel defeats the purpose of monitoring the line.