Which of the following is a criterion for successful verification of audible signal devices?

Clause 5.5.1.3 requires an audibility test to ensure sound pressure levels meet the National Building Code (typically 10 dBA above ambient, min 65 dBA).

Start free practice for ASTTBC RFPT — Fire Alarm Systems (AL)

30 questions · no signup required · 40 free questions per day

Start Practice →

Question: Which of the following is a criterion for successful verification of audible signal devices?

Answer options:

  • The signals must be 'loud enough' in the hallway
  • The signals must reach 100 dBA in every room
  • The signals must match the sound of the old system ✅ The signals must meet the sound pressure levels specified by the NBCC and the design

Correct answer: The signals must meet the sound pressure levels specified by the NBCC and the design

Explanation: Clause 5.5.1.3 requires an audibility test to ensure sound pressure levels meet the National Building Code (typically 10 dBA above ambient, min 65 dBA).