ASTTBC RFPT — Fire Alarm Systems (AL) · Question

Which method is mandatory for functionally testing a restorable heat detector?

Section 5.7.3.1.1 states that restorable heat detectors must be tested with a heat source. Use of a naked flame is prohibited.

Start free practice for ASTTBC RFPT — Fire Alarm Systems (AL)

30 questions · no signup required · 40 free questions per day

Start Practice →

Question: Which method is mandatory for functionally testing a restorable heat detector?

Answer options:

  • Canned smoke
  • Magnet test
  • Voltage meter ✅ Heat source (e.g., heat lamp)

Correct answer: Heat source (e.g., heat lamp)

Explanation: Section 5.7.3.1.1 states that restorable heat detectors must be tested with a heat source. Use of a naked flame is prohibited.