Air handling unit (AHU) shutdown initiated by duct smoke detectors must be supervised such that a fault in the control wiring results in:

S524 and NBCC require that smoke detectors located in ductwork (ancillary for fan shutdown) must also provide a trouble signal to the fire alarm panel if they a

Start free practice for ASTTBC RFPT — Fire Alarm Systems (AL)

30 questions · no signup required · 40 free questions per day

Start Practice →

Question: Air handling unit (AHU) shutdown initiated by duct smoke detectors must be supervised such that a fault in the control wiring results in:

Answer options:

  • Notification circuit signal
  • Fire department dispatch ✅ Trouble signal at the fire alarm control unit
  • Full building evacuation signal

Correct answer: Trouble signal at the fire alarm control unit

Explanation: S524 and NBCC require that smoke detectors located in ductwork (ancillary for fan shutdown) must also provide a trouble signal to the fire alarm panel if they are disconnected or fail. 13.5 refers to Fan control.