When testing an air-sampling (aspirating) smoke detector, where must the smoke simulant be introduced?

Section 5.7.4.4.2 specifies that for air-sampling systems, smoke must be introduced into the furthest sampling port of each pipe run.

Start free practice for ASTTBC RFPT — Fire Alarm Systems (AL)

30 questions · no signup required · 40 free questions per day

Start Practice →

Question: When testing an air-sampling (aspirating) smoke detector, where must the smoke simulant be introduced?

Answer options:

  • At the main detector intake only
  • At the midpoint of the pipe run ✅ At the furthest sampling port of each pipe run
  • By blowing air into the exhaust port

Correct answer: At the furthest sampling port of each pipe run

Explanation: Section 5.7.4.4.2 specifies that for air-sampling systems, smoke must be introduced into the furthest sampling port of each pipe run.