ASTTBC RFPT — Fire Alarm Systems (AL) · Question

At what height range must the operating controls of a fire alarm control unit be installed above the finished floor?

CAN/ULC-S524-19 requires the Fire Alarm Control Unit to be mounted so the display and controls are between 600 mm and 1800 mm above the finished floor.

Start free practice for ASTTBC RFPT — Fire Alarm Systems (AL)

30 questions · no signup required · 40 free questions per day

Start Practice →

Question: At what height range must the operating controls of a fire alarm control unit be installed above the finished floor?

Answer options:

  • 300 mm to 1500 mm ✅ 600 mm to 1800 mm
  • 1000 mm to 2000 mm
  • Bottom at 1200 mm

Correct answer: 600 mm to 1800 mm

Explanation: CAN/ULC-S524-19 requires the Fire Alarm Control Unit to be mounted so the display and controls are between 600 mm and 1800 mm above the finished floor.