ASTTBC RFPT — Portable Fire Extinguishers (EX) · Question

Which of the following extinguishers is exempted from the 6-year internal maintenance requirement but must still undergo hydrostatic testing every 12 years?

Per NFPA 10, Table 7.3.3.1, Halon 1211 extinguishers are exempted from the 6-year internal examination because they are closed-recovery systems; however, the cy

Start free practice for ASTTBC RFPT — Portable Fire Extinguishers (EX)

30 questions · no signup required · 40 free questions per day

Start Practice →

Question: Which of the following extinguishers is exempted from the 6-year internal maintenance requirement but must still undergo hydrostatic testing every 12 years?

Answer options:

  • Stored-pressure water-type extinguishers
  • Stored-pressure dry chemical extinguishers
  • Non-rechargeable (disposable) dry chemical extinguishers ✅ Halon 1211 extinguishers

Correct answer: Halon 1211 extinguishers

Explanation: Per NFPA 10, Table 7.3.3.1, Halon 1211 extinguishers are exempted from the 6-year internal examination because they are closed-recovery systems; however, the cylinders themselves still require a 12-year hydrostatic test.

Start free practice for ASTTBC RFPT — Portable Fire Extinguishers (EX)

30 questions · no signup required · 40 free questions per day

Start Practice →

More about ASTTBC RFPT — Portable Fire Extinguishers (EX)

Related Questions

More for ASTTBC RFPT — Portable Fire Extinguishers (EX) candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free ASTTBC RFPT — Portable Fire Extinguishers (EX) Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.