When maintaining the continuity of a shield (drain wire) through a metal junction box, what must be done with the bare wire?
ULC-S524 Clause 4.2.3.1.2 requires that in every junction box where shield continuity is maintained, the drain wires must be sleeved or insulated so they cannot
Start free practice for CFAA Fire Alarm Technician
30 questions · no signup required · 40 free questions per day
Question: When maintaining the continuity of a shield (drain wire) through a metal junction box, what must be done with the bare wire?
Answer options:
- Taped to the conduit entry ✅ Insulated/Sleeved from the box
- Soldered to the ground screw
- Cut back and removed completely
Correct answer: Insulated/Sleeved from the box
Explanation: ULC-S524 Clause 4.2.3.1.2 requires that in every junction box where shield continuity is maintained, the drain wires must be sleeved or insulated so they cannot touch the grounded box. Contact would create an illegal ground point.
Start free practice for CFAA Fire Alarm Technician
30 questions · no signup required · 40 free questions per day
More about CFAA Fire Alarm Technician
Related Questions
- The primary power for a fire alarm system must be:
- If a 120VAC primary power circuit for a fire alarm control unit is consuming 60 Watts of power, what is the cu
- In a steady-state DC circuit, if the conductor length is doubled while maintaining voltage and wire gauge, wha
- A resistor is rated at 10 Watts at 24VDC. If the voltage drops to 20VDC, what is the new power dissipation?
- A circuit has a total resistance of 40 Ohms and is connected to a 24VDC source. What is the total power dissip
- Which of the following is NOT a direct component of Ohm's Law?
More for CFAA Fire Alarm Technician candidates
Study guides
FAQs
- How long is the CFAA Fire Alarm Technician exam? — CFAA Fire Alarm Technician
- How many questions are on the CFAA Fire Alarm Technician exam? — CFAA Fire Alarm Technician
- What is the passing score for the CFAA Fire Alarm Technician exam? — CFAA Fire Alarm Technician
- How often do I need to recertify CFAA Fire Alarm Technician? — CFAA Fire Alarm Technician
Question explanations
- The primary power for a fire alarm system must be:
- If a 120VAC primary power circuit for a fire alarm control unit is consuming 60 Watts of power, what is the cu
- In a steady-state DC circuit, if the conductor length is doubled while maintaining voltage and wire gauge, wha
- A resistor is rated at 10 Watts at 24VDC. If the voltage drops to 20VDC, what is the new power dissipation?
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free CFAA Fire Alarm Technician Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.