CFAA Fire Alarm Technician · Question
When verifying a smoke detector, what is the required method to confirm its operation?
CAN/ULC-S537-19 Clause 5.5.1 requires each smoke detector to be tested in place via the introduction of smoke or aerosol to ensure response. Operating the inter
Start free practice for CFAA Fire Alarm Technician
30 questions · no signup required · 40 free questions per day
Question: When verifying a smoke detector, what is the required method to confirm its operation?
Answer options:
- Using the internal magnet test switch only ✅ Introduction of smoke or simulated smoke into the sensing chamber
- Measuring the voltage at the detector terminals
- Visual inspection of the detector's 'power on' LED
Correct answer: Introduction of smoke or simulated smoke into the sensing chamber
Explanation: CAN/ULC-S537-19 Clause 5.5.1 requires each smoke detector to be tested in place via the introduction of smoke or aerosol to ensure response. Operating the internal magnetic test switch is not sufficient for verification.
Start free practice for CFAA Fire Alarm Technician
30 questions · no signup required · 40 free questions per day
More about CFAA Fire Alarm Technician
Related Questions
- The primary power for a fire alarm system must be:
- If a 120VAC primary power circuit for a fire alarm control unit is consuming 60 Watts of power, what is the cu
- In a steady-state DC circuit, if the conductor length is doubled while maintaining voltage and wire gauge, wha
- A resistor is rated at 10 Watts at 24VDC. If the voltage drops to 20VDC, what is the new power dissipation?
- A circuit has a total resistance of 40 Ohms and is connected to a 24VDC source. What is the total power dissip
- Which of the following is NOT a direct component of Ohm's Law?
More for CFAA Fire Alarm Technician candidates
Study guides
FAQs
- How long is the CFAA Fire Alarm Technician exam? — CFAA Fire Alarm Technician
- How many questions are on the CFAA Fire Alarm Technician exam? — CFAA Fire Alarm Technician
- What is the passing score for the CFAA Fire Alarm Technician exam? — CFAA Fire Alarm Technician
- How often do I need to recertify CFAA Fire Alarm Technician? — CFAA Fire Alarm Technician
Question explanations
- The primary power for a fire alarm system must be:
- If a 120VAC primary power circuit for a fire alarm control unit is consuming 60 Watts of power, what is the cu
- In a steady-state DC circuit, if the conductor length is doubled while maintaining voltage and wire gauge, wha
- A resistor is rated at 10 Watts at 24VDC. If the voltage drops to 20VDC, what is the new power dissipation?
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free CFAA Fire Alarm Technician Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.