Electrician Red Seal · Question
What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, located in a dry room, opposite a concrete block wall?
According to CEC Rule 2-308(1) Table 6, for equipment operating at 151-600 V to ground (Condition 1, 0-150V to ground and Condition 2, 151-600V to ground) and w
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, located in a dry room, opposite a concrete block wall?
Answer options:
- 600 mm (2 ft)
- 750 mm (2.5 ft) ✅ 900 mm (3 ft)
- 1 m (3.3 ft)
Correct answer: 900 mm (3 ft)
Explanation: According to CEC Rule 2-308(1) Table 6, for equipment operating at 151-600 V to ground (Condition 1, 0-150V to ground and Condition 2, 151-600V to ground) and where exposed live parts are on one side and a grounded surface on the other (Condition 2), the minimum depth of working space is 900 mm (3 ft). A 240 Vac panel with 120 V to ground falls into Condition 2. For 0-150V to ground, Condition 1 is 750 mm. A 200A panel is typically a significant service. The correct condition for 120/240V, 200A would be condition 2 of Table 6 since a grounded concrete block wall represents a grounded surface opposite a panel, and 240V nominal voltage. Therefore, 900 mm (3 ft) is the minimum depth.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
- An electrician is installing a new 20 A, 120 V circuit for wall receptacles in a dwelling unit. Which of the f
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.