A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a 100 A, 208 V, 3-phase, 4-wire system. The bonding conductor for the system will be bare copper. What is the minimum size of the bare copper bonding conductor required for this temporary service according to the Canadian Electrical Code (CEC)?

CEC Table 16 specifies the minimum size of bonding conductors based on the rating or setting of the overcurrent device ahead of the service or feeder. For a 100

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a 100 A, 208 V, 3-phase, 4-wire system. The bonding conductor for the system will be bare copper. What is the minimum size of the bare copper bonding conductor required for this temporary service according to the Canadian Electrical Code (CEC)?

Answer options: ✅ 8 AWG copper

  • 6 AWG copper
  • 4 AWG copper
  • 10 AWG copper

Correct answer: 8 AWG copper

Explanation: CEC Table 16 specifies the minimum size of bonding conductors based on the rating or setting of the overcurrent device ahead of the service or feeder. For a 100 A service, Table 16 indicates a minimum bonding conductor size of 8 AWG copper. This ensures adequate fault current capacity for safety.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.