A plumber is installing a new kitchen sink in an existing residential dwelling. The sink drain is connected to an existing 38 mm (1 1/2 inch) trap arm that is 1.8 metres long. According to NPC guidelines, what is the maximum permissible developed length for a 38 mm trap arm from a fixture to its vent stack?
According to NPC Table 7.5.6.3., the maximum developed length for a 38 mm (1 1/2 inch) trap arm is 1.5 metres. The existing trap arm of 1.8 metres exceeds this
Start free practice for Plumber Red Seal
177 questions · no signup required · 40 free questions per day
Question: A plumber is installing a new kitchen sink in an existing residential dwelling. The sink drain is connected to an existing 38 mm (1 1/2 inch) trap arm that is 1.8 metres long. According to NPC guidelines, what is the maximum permissible developed length for a 38 mm trap arm from a fixture to its vent stack?
Answer options:
- 1.0 metre ✅ 1.5 metres
- 2.0 metres
- 2.5 metres
Correct answer: 1.5 metres
Explanation: According to NPC Table 7.5.6.3., the maximum developed length for a 38 mm (1 1/2 inch) trap arm is 1.5 metres. The existing trap arm of 1.8 metres exceeds this limit. Installing anything longer than 1.5 metres for a 38 mm trap arm is a code violation.
Start free practice for Plumber Red Seal
177 questions · no signup required · 40 free questions per day
More about Plumber Red Seal
Related Questions
- Before starting a new plumbing installation in a residential basement, what is the primary reason why a plumbe
- A plumber is installing drainage for a dishwasher in a residential kitchen. The dishwasher P-trap is located 1
- A plumber is asked to install a backflow prevention assembly on a lawn irrigation system connected to the pota
- A plumber is considering the velocity of water in a 50 mm (2") copper pipe supplying a commercial building. Ex
- A plumber is designing the domestic hot water recirculation system for a multi-story residential building. Wha
- A plumber is sizing the cold water supply for a small commercial building. The total fixture unit count for th
More for Plumber Red Seal candidates
Practice tests
Question explanations
- Before starting a new plumbing installation in a residential basement, what is the primary reason why a plumbe
- A plumber is installing drainage for a dishwasher in a residential kitchen. The dishwasher P-trap is located 1
- A plumber is asked to install a backflow prevention assembly on a lawn irrigation system connected to the pota
- A plumber is considering the velocity of water in a 50 mm (2") copper pipe supplying a commercial building. Ex
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Plumber Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.