A plumber is installing a new kitchen sink in an existing residential dwelling. The sink drain is connected to an existing 38 mm (1 1/2 inch) trap arm that is 1.8 metres long. According to NPC guidelines, what is the maximum permissible developed length for a 38 mm trap arm from a fixture to its vent stack?

According to NPC Table 7.5.6.3., the maximum developed length for a 38 mm (1 1/2 inch) trap arm is 1.5 metres. The existing trap arm of 1.8 metres exceeds this

Start free practice for Plumber Red Seal

177 questions · no signup required · 40 free questions per day

Start Practice →

Question: A plumber is installing a new kitchen sink in an existing residential dwelling. The sink drain is connected to an existing 38 mm (1 1/2 inch) trap arm that is 1.8 metres long. According to NPC guidelines, what is the maximum permissible developed length for a 38 mm trap arm from a fixture to its vent stack?

Answer options:

  • 1.0 metre ✅ 1.5 metres
  • 2.0 metres
  • 2.5 metres

Correct answer: 1.5 metres

Explanation: According to NPC Table 7.5.6.3., the maximum developed length for a 38 mm (1 1/2 inch) trap arm is 1.5 metres. The existing trap arm of 1.8 metres exceeds this limit. Installing anything longer than 1.5 metres for a 38 mm trap arm is a code violation.

Start free practice for Plumber Red Seal

177 questions · no signup required · 40 free questions per day

Start Practice →

More about Plumber Red Seal

Related Questions

More for Plumber Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Plumber Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.