Plumber Red Seal · Question
An industrial facility requires a new potable water supply line that will deliver a peak instantaneous demand of 6.0 L/s. Using a maximum allowable friction loss of 2.0 kPa per metre, what nominal pipe size (NPS) of Type L copper tubing would be appropriate according to typical plumbing sizing charts?
To determine the appropriate pipe size, a pipe sizing chart or calculator is needed, considering flow rate and friction loss. For 6.0 L/s and 2.0 kPa/m friction
Start free practice for Plumber Red Seal
177 questions · no signup required · 40 free questions per day
Question: An industrial facility requires a new potable water supply line that will deliver a peak instantaneous demand of 6.0 L/s. Using a maximum allowable friction loss of 2.0 kPa per metre, what nominal pipe size (NPS) of Type L copper tubing would be appropriate according to typical plumbing sizing charts?
Answer options:
- NPS 50 (DN 50) ✅ NPS 65 (DN 65)
- NPS 80 (DN 80)
- NPS 100 (DN 100)
Correct answer: NPS 65 (DN 65)
Explanation: To determine the appropriate pipe size, a pipe sizing chart or calculator is needed, considering flow rate and friction loss. For 6.0 L/s and 2.0 kPa/m friction loss, an NPS 65 (DN 65) pipe is typically the smallest size that would meet friction loss requirements for Type L copper. NPS 50 would result in excessive friction loss, while NPS 80 and NPS 100 would be oversized.
Start free practice for Plumber Red Seal
177 questions · no signup required · 40 free questions per day
More about Plumber Red Seal
Related Questions
- Before starting a new plumbing installation in a residential basement, what is the primary reason why a plumbe
- A plumber is installing a new kitchen sink in an existing residential dwelling. The sink drain is connected to
- A plumber is installing drainage for a dishwasher in a residential kitchen. The dishwasher P-trap is located 1
- A plumber is asked to install a backflow prevention assembly on a lawn irrigation system connected to the pota
- A plumber is considering the velocity of water in a 50 mm (2") copper pipe supplying a commercial building. Ex
- A plumber is designing the domestic hot water recirculation system for a multi-story residential building. Wha
More for Plumber Red Seal candidates
Practice tests
Question explanations
- Before starting a new plumbing installation in a residential basement, what is the primary reason why a plumbe
- A plumber is installing a new kitchen sink in an existing residential dwelling. The sink drain is connected to
- A plumber is installing drainage for a dishwasher in a residential kitchen. The dishwasher P-trap is located 1
- A plumber is asked to install a backflow prevention assembly on a lawn irrigation system connected to the pota
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Plumber Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.