Plumber Red Seal · Question
A plumber is sizing the cold water distribution piping for a small commercial building with a peak demand of 3.8 L/s. The available water pressure from the municipal supply is 480 kPa, and the highest fixture is located 12 metres above the main service entrance. The piping will be Type 'L' copper, and a maximum friction loss of 25 kPa per 30 metres of pipe is acceptable. What minimum nominal pipe size (NPS) is required for the main cold water supply line?
First, calculate the pressure loss due to elevation: 12 m * 9.81 kPa/m = 117.72 kPa. The minimum required residual pressure for most commercial fixtures is abou
Start free practice for Plumber Red Seal
177 questions · no signup required · 40 free questions per day
Question: A plumber is sizing the cold water distribution piping for a small commercial building with a peak demand of 3.8 L/s. The available water pressure from the municipal supply is 480 kPa, and the highest fixture is located 12 metres above the main service entrance. The piping will be Type 'L' copper, and a maximum friction loss of 25 kPa per 30 metres of pipe is acceptable. What minimum nominal pipe size (NPS) is required for the main cold water supply line?
Answer options:
- 1 1/4 inch
- 1 1/2 inch ✅ 2 inch
- 2 1/2 inch
Correct answer: 2 inch
Explanation: First, calculate the pressure loss due to elevation: 12 m * 9.81 kPa/m = 117.72 kPa. The minimum required residual pressure for most commercial fixtures is about 140 kPa, but even if we aim for 200 kPa for safety, the total pressure drop allowed for friction is 480 kPa - 117.72 kPa (elevation) - 200 kPa (residual) = 162.28 kPa over the entire run. Assuming a run of 60m for calculation, the allowable friction loss per 30m is 162.28 kPa / 2 = 81.14 kPa/30m. However, the question states a maximum acceptable friction loss of 25 kPa per 30 metres. Using a pipe sizing chart for Type 'L' copper and a flow rate of 3.8 L/s with a friction loss of 25 kPa/30m, a 2-inch pipe (often 50 DN) is generally the smallest size that can accommodate this flow and pressure drop. Smaller sizes would result in excessive friction loss or inadequate flow.
Start free practice for Plumber Red Seal
177 questions · no signup required · 40 free questions per day
More about Plumber Red Seal
Related Questions
- Before starting a new plumbing installation in a residential basement, what is the primary reason why a plumbe
- A plumber is installing a new kitchen sink in an existing residential dwelling. The sink drain is connected to
- A plumber is installing drainage for a dishwasher in a residential kitchen. The dishwasher P-trap is located 1
- A plumber is asked to install a backflow prevention assembly on a lawn irrigation system connected to the pota
- A plumber is considering the velocity of water in a 50 mm (2") copper pipe supplying a commercial building. Ex
- A plumber is designing the domestic hot water recirculation system for a multi-story residential building. Wha
More for Plumber Red Seal candidates
Practice tests
Question explanations
- Before starting a new plumbing installation in a residential basement, what is the primary reason why a plumbe
- A plumber is installing a new kitchen sink in an existing residential dwelling. The sink drain is connected to
- A plumber is installing drainage for a dishwasher in a residential kitchen. The dishwasher P-trap is located 1
- A plumber is asked to install a backflow prevention assembly on a lawn irrigation system connected to the pota
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Plumber Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.