A technician observes excessive subcooling at the outlet of a condenser in a direct expansion (DX) system, coupled with a higher-than-normal head pressure. What is the probable cause?

Non-condensable gases accumulate in the condenser, reducing the effective heat transfer surface. This causes an increase in condensing pressure and a proportion

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

Question: A technician observes excessive subcooling at the outlet of a condenser in a direct expansion (DX) system, coupled with a higher-than-normal head pressure. What is the probable cause?

Answer options:

  • Undercharge of refrigerant ✅ Non-condensables in the system
  • Low ambient temperature
  • Evaporator fan motor failure

Correct answer: Non-condensables in the system

Explanation: Non-condensable gases accumulate in the condenser, reducing the effective heat transfer surface. This causes an increase in condensing pressure and a proportionally higher subcooling as the refrigerant is forced to condense in a smaller area.

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

More about Refrigeration & Air Conditioning Mechanic Red Seal

Related Questions

More for Refrigeration & Air Conditioning Mechanic Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Refrigeration & Air Conditioning Mechanic Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.