A residential split-system air conditioner is experiencing recurring coil icing on the evaporator. The outdoor temperature is moderate (18°C / 64°F). What is the most probable cause requiring attention beyond simple defrosting?

A restricted liquid line filter drier reduces the amount of refrigerant flowing to the evaporator coil. This leads to a significant drop in evaporator pressure

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

Question: A residential split-system air conditioner is experiencing recurring coil icing on the evaporator. The outdoor temperature is moderate (18°C / 64°F). What is the most probable cause requiring attention beyond simple defrosting?

Answer options:

  • Excessive refrigerant charge ✅ A restricted liquid line filter drier
  • An oversized condenser unit
  • Leaky return air ductwork in an unconditioned attic

Correct answer: A restricted liquid line filter drier

Explanation: A restricted liquid line filter drier reduces the amount of refrigerant flowing to the evaporator coil. This leads to a significant drop in evaporator pressure and temperature, causing the coil to operate below freezing point and ice up, even in moderate ambient conditions.

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

More about Refrigeration & Air Conditioning Mechanic Red Seal

Related Questions

More for Refrigeration & Air Conditioning Mechanic Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Refrigeration & Air Conditioning Mechanic Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.