A refrigeration technician is called to troubleshoot a walk-in freezer operating with a discharge temperature that is consistently 20°C (36°F) higher than normal, accompanied by intermittent high-pressure cut-out trips. The system uses R404A. What is the most probable cause?

Non-condensable gases (like air or nitrogen) in the system elevate the condensing pressure and discharge temperature without contributing to refrigeration, lead

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

Question: A refrigeration technician is called to troubleshoot a walk-in freezer operating with a discharge temperature that is consistently 20°C (36°F) higher than normal, accompanied by intermittent high-pressure cut-out trips. The system uses R404A. What is the most probable cause?

Answer options:

  • Insufficient refrigerant charge.
  • Expansion valve stuck open.
  • Dirty evaporator coil. ✅ Non-condensable gases in the system.

Correct answer: Non-condensable gases in the system.

Explanation: Non-condensable gases (like air or nitrogen) in the system elevate the condensing pressure and discharge temperature without contributing to refrigeration, leading to high-pressure cut-outs and higher-than-normal discharge temperatures.

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

More about Refrigeration & Air Conditioning Mechanic Red Seal

Related Questions

More for Refrigeration & Air Conditioning Mechanic Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Refrigeration & Air Conditioning Mechanic Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.