Refrigeration & Air Conditioning Mechanic Red Seal · Question
A 230V single-phase refrigeration compressor motor has a rated full load current (FLA) of 15.0 A and a locked rotor current (LRA) of 90.0 A. What is the minimum fuse size required for motor branch circuit short-circuit and ground-fault protection, based on allowing up to 175% of FLA as per typical Canadian electrical code guidelines for non-time delay fuses, or 250% for dual-element time delay fuses, whichever is applicable and lowest standard rating below LRA?
For motor branch circuit protection, the maximum rating for a non-time delay fuse is 175% of FLA (1.75 * 15A = 26.25A which rounds to a 25A standard fuse). For
Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal
500 questions · no signup required · 40 free questions per day
Question: A 230V single-phase refrigeration compressor motor has a rated full load current (FLA) of 15.0 A and a locked rotor current (LRA) of 90.0 A. What is the minimum fuse size required for motor branch circuit short-circuit and ground-fault protection, based on allowing up to 175% of FLA as per typical Canadian electrical code guidelines for non-time delay fuses, or 250% for dual-element time delay fuses, whichever is applicable and lowest standard rating below LRA?
Answer options:
- 25 A (non-time delay fuse).
- 30 A (non-time delay fuse). ✅ 40 A (time delay fuse).
- 60 A (non-time delay fuse).
Correct answer: 40 A (time delay fuse).
Explanation: For motor branch circuit protection, the maximum rating for a non-time delay fuse is 175% of FLA (1.75 * 15A = 26.25A which rounds to a 25A standard fuse). For a time-delay fuse, it's 250% of FLA (2.5 * 15A = 37.5A which rounds up to a 40A standard fuse). The selected fuse must also be less than the LRA (90A). So 40A time delay is the appropriate choice as it allows for starting current while offering protection, and is lower than the 60A potential for a standard non-time delay fuse if selected by the wrong percentage.
Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal
500 questions · no signup required · 40 free questions per day
More about Refrigeration & Air Conditioning Mechanic Red Seal
Related Questions
- Which of the following refrigerants is a hydrofluorocarbon (HFC) and has a high ozone depletion potential (ODP
- Which component is responsible for compressing the refrigerant vapour to a high pressure and temperature?
- According to the Canadian Electrical Code (CEC), what is the minimum required working clearance in front of el
- What is the main operating characteristic difference between a fixed orifice (capillary tube) and a Thermostat
- Which type of electric motor requires a capacitor for starting and running, offering higher efficiency and bet
- When evacuating a refrigeration system, what is the recommended deep vacuum level, typically measured in micro
More for Refrigeration & Air Conditioning Mechanic Red Seal candidates
FAQs
Question explanations
- Which of the following refrigerants is a hydrofluorocarbon (HFC) and has a high ozone depletion potential (ODP
- Which component is responsible for compressing the refrigerant vapour to a high pressure and temperature?
- According to the Canadian Electrical Code (CEC), what is the minimum required working clearance in front of el
- What is the main operating characteristic difference between a fixed orifice (capillary tube) and a Thermostat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Refrigeration & Air Conditioning Mechanic Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.