Refrigeration & Air Conditioning Mechanic Red Seal · Question
A refrigeration system with an R-410A condensing unit is located on a rooftop 15 metres above the evaporator, which is rated for 30,000 BTU/hr (8.79 kW). The manufacturer specifies a maximum suction line pressure drop equivalent to 2 K (2°C) temperature glid. Using a reputable piping design chart for R-410A, which of the following nominal copper tube sizes for the suction line (OD indicated) would most likely meet the pressure drop requirements without excessive oil return issues?
For a 30,000 BTU/hr R-410A system with a 15-meter vertical lift, a 1 1/8 inch (28.58 mm) suction line offers an appropriate balance between minimizing pressure
Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal
500 questions · no signup required · 40 free questions per day
Question: A refrigeration system with an R-410A condensing unit is located on a rooftop 15 metres above the evaporator, which is rated for 30,000 BTU/hr (8.79 kW). The manufacturer specifies a maximum suction line pressure drop equivalent to 2 K (2°C) temperature glid. Using a reputable piping design chart for R-410A, which of the following nominal copper tube sizes for the suction line (OD indicated) would most likely meet the pressure drop requirements without excessive oil return issues?
Answer options: ✅ 1 1/8 inch (28.58 mm)
- 7/8 inch (22.23 mm)
- 5/8 inch (15.88 mm)
- 1 3/8 inch (34.93 mm)
Correct answer: 1 1/8 inch (28.58 mm)
Explanation: For a 30,000 BTU/hr R-410A system with a 15-meter vertical lift, a 1 1/8 inch (28.58 mm) suction line offers an appropriate balance between minimizing pressure drop (crucial for capacity and efficiency) and maintaining sufficient gas velocity for oil return, as determined by piping design charts. A smaller line would lead to excessive pressure drop, while a larger line could compromise oil return on the vertical lift.
Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal
500 questions · no signup required · 40 free questions per day
More about Refrigeration & Air Conditioning Mechanic Red Seal
Related Questions
- Which of the following refrigerants is a hydrofluorocarbon (HFC) and has a high ozone depletion potential (ODP
- Which component is responsible for compressing the refrigerant vapour to a high pressure and temperature?
- According to the Canadian Electrical Code (CEC), what is the minimum required working clearance in front of el
- What is the main operating characteristic difference between a fixed orifice (capillary tube) and a Thermostat
- Which type of electric motor requires a capacitor for starting and running, offering higher efficiency and bet
- When evacuating a refrigeration system, what is the recommended deep vacuum level, typically measured in micro
More for Refrigeration & Air Conditioning Mechanic Red Seal candidates
FAQs
Question explanations
- Which of the following refrigerants is a hydrofluorocarbon (HFC) and has a high ozone depletion potential (ODP
- Which component is responsible for compressing the refrigerant vapour to a high pressure and temperature?
- According to the Canadian Electrical Code (CEC), what is the minimum required working clearance in front of el
- What is the main operating characteristic difference between a fixed orifice (capillary tube) and a Thermostat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Refrigeration & Air Conditioning Mechanic Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.