A falsework system for a 4.5 m high concrete wall features vertical shores. What is the minimum recommendation for the slenderness ratio (L/r) for compression members, such as these shores, to ensure stability, according to CSA S269.3 guidelines for falsework design?

CSA S269.3, Clause 9.6.1 states that the slenderness ratio (L/r) for timber compression members in falsework should not exceed 100, and for steel, it should not

Start free practice for Carpenter Red Seal Exam Prep

300 questions · no signup required · 40 free questions per day

Start Practice →

Question: A falsework system for a 4.5 m high concrete wall features vertical shores. What is the minimum recommendation for the slenderness ratio (L/r) for compression members, such as these shores, to ensure stability, according to CSA S269.3 guidelines for falsework design?

Answer options:

  • Should not exceed 50. ✅ Should not exceed 100 for timber members.
  • Should not exceed 200.
  • Slenderness ratio is not a direct concern for vertical shores.

Correct answer: Should not exceed 100 for timber members.

Explanation: CSA S269.3, Clause 9.6.1 states that the slenderness ratio (L/r) for timber compression members in falsework should not exceed 100, and for steel, it should not exceed 200. This limit helps prevent buckling failures.

Start free practice for Carpenter Red Seal Exam Prep

300 questions · no signup required · 40 free questions per day

Start Practice →

More about Carpenter Red Seal Exam Prep

Related Questions

More for Carpenter Red Seal Exam Prep candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Carpenter Red Seal Exam Prep Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.