CFAA Fire Alarm Technician · Question

When installed in a separate enclosure, at what height should an End-of-Line (EOL) device be mounted?

S524 Clause 5.12.1.1 states the end-of-line resistor or device must be located between 1200 mm and 1800 mm for easy access/maintenance.

Start free practice for CFAA Fire Alarm Technician

30 questions · no signup required · 40 free questions per day

Start Practice →

Question: When installed in a separate enclosure, at what height should an End-of-Line (EOL) device be mounted?

Answer options:

  • Between 500 mm and 1000 mm
  • Between 1000 mm and 1500 mm ✅ Between 1200 mm and 1800 mm
  • Between 1800 mm and 2400 mm

Correct answer: Between 1200 mm and 1800 mm

Explanation: S524 Clause 5.12.1.1 states the end-of-line resistor or device must be located between 1200 mm and 1800 mm for easy access/maintenance.

Start free practice for CFAA Fire Alarm Technician

30 questions · no signup required · 40 free questions per day

Start Practice →