Following two consecutive sensitivity tests where the detector remains within its range, what is the maximum allowable interval for subsequent sensitivity tests?

Clause 5.7.4.1.3 allows the frequency to be extended to 5 years if the device remains within range for two consecutive tests (the initial 1-year and the first 2

Start free practice for CFAA Fire Alarm Technician

30 questions · no signup required · 40 free questions per day

Start Practice →

Question: Following two consecutive sensitivity tests where the detector remains within its range, what is the maximum allowable interval for subsequent sensitivity tests?

Answer options:

  • 3 years
  • 4 years ✅ 5 years
  • 7 years

Correct answer: 5 years

Explanation: Clause 5.7.4.1.3 allows the frequency to be extended to 5 years if the device remains within range for two consecutive tests (the initial 1-year and the first 2-year cycle).