Calculate the minimum battery capacity (Ah) including a 1.25 safety factor for a system with a 0.5A standby load and a 2.0A alarm load (30-min alarm duration).

The battery must support the system for 24 hours of standby followed by 30 minutes of alarm. 0.5A * 24h = 12Ah. 2.0A * 0.5h = 1Ah. Total = 13Ah. Applying the sa

Start free practice for CFAA Fire Alarm Technician

30 questions · no signup required · 40 free questions per day

Start Practice →

Question: Calculate the minimum battery capacity (Ah) including a 1.25 safety factor for a system with a 0.5A standby load and a 2.0A alarm load (30-min alarm duration).

Answer options:

  • 13.0 Ah ✅ 16.25 Ah
  • 18.5 Ah
  • 24.0 Ah

Correct answer: 16.25 Ah

Explanation: The battery must support the system for 24 hours of standby followed by 30 minutes of alarm. 0.5A * 24h = 12Ah. 2.0A * 0.5h = 1Ah. Total = 13Ah. Applying the safety factor (1.25) = 16.25Ah.