When using PVC conduit for fire alarm wiring, how is the bonding of metal device boxes achieved?

Non-metallic raceways (PVC) do not provide an electrical path to ground, so a separate bonding conductor must be pulled in the raceway to bond all metal enclosu

Start free practice for CFAA Fire Alarm Technician

30 questions · no signup required · 40 free questions per day

Start Practice →

Question: When using PVC conduit for fire alarm wiring, how is the bonding of metal device boxes achieved?

Answer options:

  • No bonding is required
  • Bonding is only required for high voltage ✅ A separate bonding conductor must be installed
  • The drain wire of the FAS cable is used as the bond

Correct answer: A separate bonding conductor must be installed

Explanation: Non-metallic raceways (PVC) do not provide an electrical path to ground, so a separate bonding conductor must be pulled in the raceway to bond all metal enclosures (pull stations, etc.) per CEC Rule 10-402.