What is the maximum allowable distance for an unsupervised circuit between a fire alarm relay and its ancillary load?

If the circuit between the fire alarm relay and the fan starter is not supervised, S524 requires the relay to be located within 1 meter and the wiring to be in

Start free practice for CFAA Fire Alarm Technician

30 questions · no signup required · 40 free questions per day

Start Practice →

Question: What is the maximum allowable distance for an unsupervised circuit between a fire alarm relay and its ancillary load?

Answer options:

  • No limit, as long as it's in conduit
  • 3 meters ✅ 1 meter
  • 10 meters

Correct answer: 1 meter

Explanation: If the circuit between the fire alarm relay and the fan starter is not supervised, S524 requires the relay to be located within 1 meter and the wiring to be in conduit.