What is the minimum clearance required between a smoke detector and an air supply diffuser?

Water pumps and air conditioners can create high air velocity or dust that may cause nuisance alarms or prevent smoke entry into the chamber. 1.0m is the standa

Start free practice for CFAA Fire Alarm Technician

30 questions · no signup required · 40 free questions per day

Start Practice →

Question: What is the minimum clearance required between a smoke detector and an air supply diffuser?

Answer options:

  • 300 mm
  • 500 mm
  • 2.0 meters ✅ 1.0 meter

Correct answer: 1.0 meter

Explanation: Water pumps and air conditioners can create high air velocity or dust that may cause nuisance alarms or prevent smoke entry into the chamber. 1.0m is the standard clearance.