A system has a standby current of 0.5A and an alarm current of 2.0A. Calculate the minimum Ah required for 24 hours standby and 5 minutes alarm (excluding safety factor).

Standby: 0.5A x 24h = 12Ah. Alarm: 2.0A x (5/60)h = 0.166Ah. Total = 12.166Ah. Multiplying by a standard 1.25 safety factor (S524 requirement) = ~15.2 Ah. Neare

Start free practice for CFAA Fire Alarm Technician

30 questions · no signup required · 40 free questions per day

Start Practice →

Question: A system has a standby current of 0.5A and an alarm current of 2.0A. Calculate the minimum Ah required for 24 hours standby and 5 minutes alarm (excluding safety factor).

Answer options:

  • 2.5 Ah
  • 12.0 Ah ✅ 12.17 Ah
  • 48.0 Ah

Correct answer: 12.17 Ah

Explanation: Standby: 0.5A x 24h = 12Ah. Alarm: 2.0A x (5/60)h = 0.166Ah. Total = 12.166Ah. Multiplying by a standard 1.25 safety factor (S524 requirement) = ~15.2 Ah. Nearest higher standard size is preferred. Base calculation is 12.17 Ah.