Which of the following heights for a wall-mounted strobe light center-line would be a violation of CAN/ULC-S524?

Clause 5.10.1.2 specifies wall-mounted visible signals shall be between 2000 mm and 2400 mm, unless ceiling mounted. 1900 mm is below the minimum.

Start free practice for CFAA Fire Alarm Technician

30 questions · no signup required · 40 free questions per day

Start Practice →

Question: Which of the following heights for a wall-mounted strobe light center-line would be a violation of CAN/ULC-S524?

Answer options:

  • 2000 mm
  • 2200 mm
  • 2400 mm ✅ 1900 mm

Correct answer: 1900 mm

Explanation: Clause 5.10.1.2 specifies wall-mounted visible signals shall be between 2000 mm and 2400 mm, unless ceiling mounted. 1900 mm is below the minimum.