On a peaked ceiling, within what horizontal distance of the peak must the first row of smoke detectors be located?

CAN/ULC-S524:2019 Clause 5.7.5.1 states that for peaked ceilings, a row of detectors shall be located at or within 900 mm of the peak.

Start free practice for CFAA Fire Alarm Technician

30 questions · no signup required · 40 free questions per day

Start Practice →

Question: On a peaked ceiling, within what horizontal distance of the peak must the first row of smoke detectors be located?

Answer options:

  • 300 mm
  • 500 mm
  • 750 mm ✅ 900 mm

Correct answer: 900 mm

Explanation: CAN/ULC-S524:2019 Clause 5.7.5.1 states that for peaked ceilings, a row of detectors shall be located at or within 900 mm of the peak.