What is the minimum horizontal separation required for Class A outgoing and return conductors in a non-sprinklered building?

CAN/ULC-S524 requires Class A conductors to be separated by at least 1200mm horizontally and 300mm vertically unless permitted otherwise (e.g., entering/exiting

Start free practice for CFAA Fire Alarm Technician

30 questions · no signup required · 40 free questions per day

Start Practice →

Question: What is the minimum horizontal separation required for Class A outgoing and return conductors in a non-sprinklered building?

Answer options:

  • 300 mm circuits
  • 600 mm circuits
  • 900 mm circuits ✅ 1200 mm circuits

Correct answer: 1200 mm circuits

Explanation: CAN/ULC-S524 requires Class A conductors to be separated by at least 1200mm horizontally and 300mm vertically unless permitted otherwise (e.g., entering/exiting a room).