In a large high-rise, which communication circuit class is required for an addressable FACP loop to ensure a single open circuit does not result in the loss of communication to all devices?

Data communication links (DCL) that use active field devices and serve multiple zones/floors must be wired as DCLB (redundant path) or DCLC to ensure a single b

Start free practice for CFAA Fire Alarm Technician

30 questions · no signup required · 40 free questions per day

Start Practice →

Question: In a large high-rise, which communication circuit class is required for an addressable FACP loop to ensure a single open circuit does not result in the loss of communication to all devices?

Answer options: ✅ DCLB or DCLC

  • DCLA only
  • Conventional Class B only
  • Parallel Data Link

Correct answer: DCLB or DCLC

Explanation: Data communication links (DCL) that use active field devices and serve multiple zones/floors must be wired as DCLB (redundant path) or DCLC to ensure a single break doesn't disable the whole system.