What is the requirement for the wiring between a fire alarm relay and a fan motor starter if the relay is located 3 meters away?

Under S524, if the relay is within 900mm of the device and the wiring is in conduit, it is acceptable. If it is further away, the circuit must be supervised for

Start free practice for CFAA Fire Alarm Technician

30 questions · no signup required · 40 free questions per day

Start Practice →

Question: What is the requirement for the wiring between a fire alarm relay and a fan motor starter if the relay is located 3 meters away?

Answer options:

  • It must be installed in a separate red box
  • It must be monitored for a ground fault only ✅ It must be supervised for open/short circuits if it is further than 900mm from the device
  • It must be powered by a separate circuit breaker

Correct answer: It must be supervised for open/short circuits if it is further than 900mm from the device

Explanation: Under S524, if the relay is within 900mm of the device and the wiring is in conduit, it is acceptable. If it is further away, the circuit must be supervised for integrity.