Per CAN/ULC-S536, sealing lead-acid batteries must be replaced if they fail a capacity test, but what is the recommended replacement interval if manufacturer instructions are absent?

Clause 5.5.3 requires battery capacity testing annually. If a battery fails to meet its 24-hour standby and subsequent 30-minute alarm capacity, it must be repl

Start free practice for CFAA Fire Alarm Technician

30 questions · no signup required · 40 free questions per day

Start Practice →

Question: Per CAN/ULC-S536, sealing lead-acid batteries must be replaced if they fail a capacity test, but what is the recommended replacement interval if manufacturer instructions are absent?

Answer options:

  • Every year
  • Every 2 years ✅ Every 5 years
  • Every 10 years

Correct answer: Every 5 years

Explanation: Clause 5.5.3 requires battery capacity testing annually. If a battery fails to meet its 24-hour standby and subsequent 30-minute alarm capacity, it must be replaced. Batteries 5 years old or older must also be carefully evaluated or replaced per manufacturer specs.