Electrician Red Seal · Question
A proximity sensor connected to a PLC input is designed to detect metallic objects. The sensor has a maximum sensing distance of 20 mm. During operation, a metallic target passes within 15 mm of the sensor, but the PLC input does not register a state change. The sensor's supply voltage is confirmed to be correct. What is a possible cause?
Even if the target is within the sensing range, an incompatible output type (e.g., NPN sensor to a PNP input, or current sink to current source) would prevent t
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A proximity sensor connected to a PLC input is designed to detect metallic objects. The sensor has a maximum sensing distance of 20 mm. During operation, a metallic target passes within 15 mm of the sensor, but the PLC input does not register a state change. The sensor's supply voltage is confirmed to be correct. What is a possible cause?
Answer options:
- The target is moving too slowly for the sensor to detect. ✅ The sensor's output type is incompatible with the PLC input module.
- The sensor is configured for non-metallic object detection.
- The PLC ladder logic incorrectly reads the input status.
Correct answer: The sensor's output type is incompatible with the PLC input module.
Explanation: Even if the target is within the sensing range, an incompatible output type (e.g., NPN sensor to a PNP input, or current sink to current source) would prevent the PLC input from registering a valid signal. Target speed is usually a factor for very high-speed applications, and a proximity sensor is specific to metallic or non-metallic objects, not switchable in this context. Incorrect PLC logic would be the next step if hardware compatibility is ruled out.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.