An electrician is installing a 3-wire, 120/240 V feeder supplying a subpanel in a detached garage, which contains only 120 V loads. The main service is a 4-wire, 120/240 V system with a grounded neutral. What is the correct method for connecting the neutral and grounding conductors at the detached garage subpanel according to the CEC?

Rule 10-208(b) of the CEC requires that for a feeder supplying a detached building from a main service that is a 4-wire system with a grounded neutral, the neut

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: An electrician is installing a 3-wire, 120/240 V feeder supplying a subpanel in a detached garage, which contains only 120 V loads. The main service is a 4-wire, 120/240 V system with a grounded neutral. What is the correct method for connecting the neutral and grounding conductors at the detached garage subpanel according to the CEC?

Answer options:

  • Bond the neutral bus to the enclosure and install a separate grounding electrode.
  • Isolate the neutral bus from the enclosure and bond the neutral to the grounding electrode. ✅ Isolate the neutral bus from the enclosure and bond the grounding conductor to the enclosure, with a separate grounding electrode.
  • Bond both the neutral bus and the grounding conductor to the enclosure, with a separate grounding electrode.

Correct answer: Isolate the neutral bus from the enclosure and bond the grounding conductor to the enclosure, with a separate grounding electrode.

Explanation: Rule 10-208(b) of the CEC requires that for a feeder supplying a detached building from a main service that is a 4-wire system with a grounded neutral, the neutral conductor must be isolated from the enclosure at the subpanel. The equipment grounding conductor must be bonded to the enclosure, and a separate grounding electrode must be installed at the detached building and bonded to the enclosure. This prevents parallel paths for neutral current on the grounding system.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.