A licensed electrician is installing a new 200 A service entrance for a single-family dwelling. According to the Canadian Electrical Code (CEC), what is the minimum acceptable size for the copper bonding conductor connecting the service neutral to the grounding electrode system if the service conductors are 3/0 AWG copper?

CEC Rule 10-612(1)(a) requires the bonding conductor for services to be sized according to Table 16, based on the service conductor size. For 3/0 AWG copper ser

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: A licensed electrician is installing a new 200 A service entrance for a single-family dwelling. According to the Canadian Electrical Code (CEC), what is the minimum acceptable size for the copper bonding conductor connecting the service neutral to the grounding electrode system if the service conductors are 3/0 AWG copper?

Answer options:

  • No. 6 AWG copper
  • No. 4 AWG copper ✅ No. 2 AWG copper
  • No. 1/0 AWG copper

Correct answer: No. 2 AWG copper

Explanation: CEC Rule 10-612(1)(a) requires the bonding conductor for services to be sized according to Table 16, based on the service conductor size. For 3/0 AWG copper service conductors, Table 16 specifies a minimum No. 2 AWG copper bonding conductor. A No. 6 AWG copper conductor would be suitable for a smaller service, typically up to 100 A with No. 2 AWG copper service conductors.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.