A technician is installing a new 45 A, 208 V, three-phase motor on a permanent basis in a dry industrial environment. The motor leads are connected to a junction box containing the circuit conductors, which are run in rigid metal conduit (RMC). The circuit conductors are 75 °C insulated copper. Which of the following conductor sizes is the minimum permissible for this motor branch circuit, considering continuous operation and standard overcurrent protection?
CEC Rule 28-106(1) states that conductors for motor branch circuits must have an ampacity not less than 125% of the motor's full-load current (FLC). For a 45 A
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A technician is installing a new 45 A, 208 V, three-phase motor on a permanent basis in a dry industrial environment. The motor leads are connected to a junction box containing the circuit conductors, which are run in rigid metal conduit (RMC). The circuit conductors are 75 °C insulated copper. Which of the following conductor sizes is the minimum permissible for this motor branch circuit, considering continuous operation and standard overcurrent protection?
Answer options:
- No. 10 AWG copper
- No. 8 AWG copper ✅ No. 6 AWG copper
- No. 4 AWG copper
Correct answer: No. 6 AWG copper
Explanation: CEC Rule 28-106(1) states that conductors for motor branch circuits must have an ampacity not less than 125% of the motor's full-load current (FLC). For a 45 A motor, 1.25 x 45 A = 56.25 A. According to CEC Table 2 (75 °C column), a No. 6 AWG copper conductor has an ampacity of 65 A, which meets this requirement. No. 8 AWG has an ampacity of 50 A, which is insufficient.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.