An industrial facility is being upgraded, and an electrician needs to install a new circuit for a hazardous location identified as Class I, Division 2, Group C. The circuit will be a 240 V, 20 A branch circuit with copper conductors. What type of wiring method is explicitly permitted for this installation according to CEC Section 18 when installed with explosion-proof fittings?
CEC Rule 18-106(1) outlines permissible wiring methods for Class I, Division 2 locations. Among the listed options, Teck 90 armoured cable is explicitly permitt
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: An industrial facility is being upgraded, and an electrician needs to install a new circuit for a hazardous location identified as Class I, Division 2, Group C. The circuit will be a 240 V, 20 A branch circuit with copper conductors. What type of wiring method is explicitly permitted for this installation according to CEC Section 18 when installed with explosion-proof fittings?
Answer options:
- Rigid PVC conduit (RW90)
- Electrical metallic tubing (EMT) ✅ Teck 90 armoured cable
- Non-metallic sheathed cable (NMD90)
Correct answer: Teck 90 armoured cable
Explanation: CEC Rule 18-106(1) outlines permissible wiring methods for Class I, Division 2 locations. Among the listed options, Teck 90 armoured cable is explicitly permitted as per Rule 18-106(1)(e). Rigid PVC conduit is generally prohibited (Rule 18-004(1)), EMT is not permitted unless it also meets other specific criteria for Class I, Division 2 (Rules 18-104(2)(b) and (c) for Class I Div 1, not applicable for general Div 2), and NMD90 cable is not suitable for hazardous locations.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.