Electrician Red Seal · Question
A three-phase, 480 V motor is controlled by a magnetic starter with an across-the-line configuration. The motor is rated for 15 kW (approximately 20 HP). The electrician needs to select appropriate overload heaters for the motor. The motor's nameplate indicates a Service Factor (SF) of 1.15 and a Full Load Amperage (FLA) of 27 A. According to the CEC, which of the following is the correct maximum setting for the overload protection if the motor has a service factor of 1.15 or greater?
According to CEC Rule 28-306(1) and Table 30, for a motor with a service factor of 1.15 or more, the maximum setting for the overload protection shall not excee
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A three-phase, 480 V motor is controlled by a magnetic starter with an across-the-line configuration. The motor is rated for 15 kW (approximately 20 HP). The electrician needs to select appropriate overload heaters for the motor. The motor's nameplate indicates a Service Factor (SF) of 1.15 and a Full Load Amperage (FLA) of 27 A. According to the CEC, which of the following is the correct maximum setting for the overload protection if the motor has a service factor of 1.15 or greater?
Answer options:
- 27 A
- 30 A
- 31.05 A ✅ 34.1 A
Correct answer: 34.1 A
Explanation: According to CEC Rule 28-306(1) and Table 30, for a motor with a service factor of 1.15 or more, the maximum setting for the overload protection shall not exceed 125% of the motor's full-load current rating. Therefore, 27 A * 1.25 = 33.75 A. The closest available standard heater size without exceeding this value must be chosen, or in this context, the calculated maximum value is 33.75A, so 34.1 A is the closest option if selecting from standard available settings.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.