A pump motor controlled by a float switch occasionally fails to start, but the main circuit breaker is not tripped. When the float switch indicates 'high water', an electrician measures 120 V AC at the input of the control transformer, but 0 V AC at the output. What is the most probable cause?
If there is voltage at the transformer primary but none at the secondary, it indicates an open circuit within the transformer windings (either primary or second
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A pump motor controlled by a float switch occasionally fails to start, but the main circuit breaker is not tripped. When the float switch indicates 'high water', an electrician measures 120 V AC at the input of the control transformer, but 0 V AC at the output. What is the most probable cause?
Answer options:
- The float switch contacts are stuck open
- The motor has a winding short to ground ✅ The control transformer's primary or secondary winding is open
- The motor contactor coil is shorted
Correct answer: The control transformer's primary or secondary winding is open
Explanation: If there is voltage at the transformer primary but none at the secondary, it indicates an open circuit within the transformer windings (either primary or secondary) or a blown internal fuse, preventing voltage transformation. A stuck float switch would prevent current to the transformer primary. Motor winding shorts or contactor coil shorts would cause current draw, potentially tripping a breaker, but not necessarily zero output from a transformer with input voltage.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.