Electrician Red Seal · Question
A technician is troubleshooting a three-phase motor control circuit. The PLC output for the motor starter coil energizes, but the motor does not start, and the starter's auxiliary contacts are not changing state. A Voltmeter across terminals A1 and A2 of the starter coil reads 120 V AC. What is the most likely issue?
If the PLC output is energizing and 120 V AC is measured across the starter coil, but the starter does not pull in, it indicates that the coil itself is open-ci
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A technician is troubleshooting a three-phase motor control circuit. The PLC output for the motor starter coil energizes, but the motor does not start, and the starter's auxiliary contacts are not changing state. A Voltmeter across terminals A1 and A2 of the starter coil reads 120 V AC. What is the most likely issue?
Answer options:
- The motor has an open winding.
- The starter's overload protection has tripped. ✅ The starter coil is open-circuited.
- There is a phase imbalance in the supply voltage.
Correct answer: The starter coil is open-circuited.
Explanation: If the PLC output is energizing and 120 V AC is measured across the starter coil, but the starter does not pull in, it indicates that the coil itself is open-circuited. An open coil will not create a magnetic field to close the contacts, even if voltage is applied. Options 1, 2, and 4 would not prevent the starter coil from energizing if voltage was present across it.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.