Electrician Red Seal · Question
When troubleshooting a motor starter that fails to energize, a technician uses a multimeter to check for control voltage. If 120 V AC is present at the common terminal of the start/stop pushbutton station but not at the coil of the motor starter, which component should be checked next?
If voltage is present up to the common of the start/stop station but not at the coil, the break in the circuit must be between these two points. Typical compone
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: When troubleshooting a motor starter that fails to energize, a technician uses a multimeter to check for control voltage. If 120 V AC is present at the common terminal of the start/stop pushbutton station but not at the coil of the motor starter, which component should be checked next?
Answer options:
- The motor windings.
- The main power circuit fuses. ✅ Continuity through the stop pushbutton and overload contacts.
- The PLC output module.
Correct answer: Continuity through the stop pushbutton and overload contacts.
Explanation: If voltage is present up to the common of the start/stop station but not at the coil, the break in the circuit must be between these two points. Typical components in series in this control voltage path, after the start/stop station and before the coil, include the normally closed (NC) stop pushbutton contacts, any emergency stop buttons, and the NC auxiliary contacts of the thermal overload relay. Checking continuity through these components will identify the open circuit.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.