Electrician Red Seal · Question
A technician is troubleshooting a motor control circuit where a 3-phase induction motor fails to start. The control circuit uses a 24 V AC control supply, a normally open (N.O.) start button, a normally closed (N.C.) stop button, and a contactor coil (CR-1). When the start button is pressed, the contactor energizes, but the motor de-energizes immediately upon releasing the start button. What is the most likely cause?
If the contactor energizes when the start button is pressed but de-energizes upon release, it indicates that the holding circuit (also known as the seal-in or l
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A technician is troubleshooting a motor control circuit where a 3-phase induction motor fails to start. The control circuit uses a 24 V AC control supply, a normally open (N.O.) start button, a normally closed (N.C.) stop button, and a contactor coil (CR-1). When the start button is pressed, the contactor energizes, but the motor de-energizes immediately upon releasing the start button. What is the most likely cause?
Answer options: ✅ The holding contact for CR-1 is faulty or miswired.
- The stop button is wired incorrectly (N.O. instead of N.C.).
- The overload relay contacts are open.
- The motor's thermal protectors have tripped.
Correct answer: The holding contact for CR-1 is faulty or miswired.
Explanation: If the contactor energizes when the start button is pressed but de-energizes upon release, it indicates that the holding circuit (also known as the seal-in or latching circuit) for the contactor is not maintaining the coil's energization. This holding circuit typically involves a N.O. auxiliary contact of the contactor wired in parallel with the start button.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.