A utility pole carrying 14.4 kV primary distribution lines has multiple ground rods driven at its base. What is the maximum permissible resistance to ground for the grounding electrode system at this location, according to Canadian Electrical Code (CEC) Rule 10-100?
CEC Rule 10-100(1) specifies that a grounding electrode system for supply circuits operating at more than 750 V (such as 14.4 kV) shall have a resistance to gro
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A utility pole carrying 14.4 kV primary distribution lines has multiple ground rods driven at its base. What is the maximum permissible resistance to ground for the grounding electrode system at this location, according to Canadian Electrical Code (CEC) Rule 10-100?
Answer options: ✅ 5 Ohms
- 10 Ohms
- 25 Ohms
- Depends on soil resistivity, no fixed maximum
Correct answer: 5 Ohms
Explanation: CEC Rule 10-100(1) specifies that a grounding electrode system for supply circuits operating at more than 750 V (such as 14.4 kV) shall have a resistance to ground not exceeding 5 Ohms. This lower resistance provides a more effective path for high-voltage fault currents.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.