An electrician is tasked with bonding a new, non-current-carrying metal exhaust fan housing in a hazardous location (Class I, Division 2). The fan is rated for 240 V, 3-phase, 10 A. What is the minimum size copper bonding conductor required for this application?
The minimum size bonding conductor for equipment is determined by the rating of the overcurrent device protecting the circuit. For a 10 A motor, the overcurrent
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: An electrician is tasked with bonding a new, non-current-carrying metal exhaust fan housing in a hazardous location (Class I, Division 2). The fan is rated for 240 V, 3-phase, 10 A. What is the minimum size copper bonding conductor required for this application?
Answer options:
- #14 AWG
- #12 AWG ✅ #10 AWG
- #8 AWG
Correct answer: #10 AWG
Explanation: The minimum size bonding conductor for equipment is determined by the rating of the overcurrent device protecting the circuit. For a 10 A motor, the overcurrent device protecting the feeder/branch circuit would typically be 15 A or 20 A. According to CEC Table 16, a 20 A overcurrent device requires a minimum #10 AWG copper bonding conductor. Hazard location requirements may necessitate specific wiring methods but not larger bonding conductor sizes unless otherwise specified.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.