Electrician Red Seal · Question

An electrician is tasked with bonding a new, non-current-carrying metal exhaust fan housing in a hazardous location (Class I, Division 2). The fan is rated for 240 V, 3-phase, 10 A. What is the minimum size copper bonding conductor required for this application?

The minimum size bonding conductor for equipment is determined by the rating of the overcurrent device protecting the circuit. For a 10 A motor, the overcurrent

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: An electrician is tasked with bonding a new, non-current-carrying metal exhaust fan housing in a hazardous location (Class I, Division 2). The fan is rated for 240 V, 3-phase, 10 A. What is the minimum size copper bonding conductor required for this application?

Answer options:

  • #14 AWG
  • #12 AWG ✅ #10 AWG
  • #8 AWG

Correct answer: #10 AWG

Explanation: The minimum size bonding conductor for equipment is determined by the rating of the overcurrent device protecting the circuit. For a 10 A motor, the overcurrent device protecting the feeder/branch circuit would typically be 15 A or 20 A. According to CEC Table 16, a 20 A overcurrent device requires a minimum #10 AWG copper bonding conductor. Hazard location requirements may necessitate specific wiring methods but not larger bonding conductor sizes unless otherwise specified.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.