A single-phase, 120/240 V service entrance is being installed for a small workshop. The service conductors are #2 AWG copper. What is the minimum size copper main grounding conductor (grounding electrode conductor) required to connect the neutral terminal to the grounding electrode system, assuming a driven ground rod is used?

According to CEC Rule 10-114 and Table 17, for service conductors up to #2 AWG copper, the minimum size copper grounding electrode conductor for a driven ground

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: A single-phase, 120/240 V service entrance is being installed for a small workshop. The service conductors are #2 AWG copper. What is the minimum size copper main grounding conductor (grounding electrode conductor) required to connect the neutral terminal to the grounding electrode system, assuming a driven ground rod is used?

Answer options:

  • #8 AWG ✅ #6 AWG
  • #4 AWG
  • #2 AWG

Correct answer: #6 AWG

Explanation: According to CEC Rule 10-114 and Table 17, for service conductors up to #2 AWG copper, the minimum size copper grounding electrode conductor for a driven ground rod (not connected to a continuous metallic underground water pipe) is #6 AWG. If the service conductors were larger than #2 AWG, the grounding conductor would also increase.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.