Electrician Red Seal · Question
An electrician is installing a sub-panel in a detached garage, fed by a 60 A, 120/240 V feeder from the main service panel in the house. How should the grounded (neutral) conductor and the equipment grounding conductor be handled in the sub-panel?
In a sub-panel in a detached building, the neutral bus must be isolated from the panel enclosure and the equipment grounding bus. The equipment grounding conduc
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: An electrician is installing a sub-panel in a detached garage, fed by a 60 A, 120/240 V feeder from the main service panel in the house. How should the grounded (neutral) conductor and the equipment grounding conductor be handled in the sub-panel?
Answer options:
- The neutral bus and the equipment grounding bus must be bonded together. ✅ The neutral bus must be isolated from the equipment grounding bus, and the equipment grounding conductor must terminate on its own bus.
- Both the neutral and ground conductors should be terminated on the neutral bus, which is isolated from the panel enclosure.
- Only the phase conductors and the neutral conductor are required; a separate grounding conductor is not needed for a sub-panel.
Correct answer: The neutral bus must be isolated from the equipment grounding bus, and the equipment grounding conductor must terminate on its own bus.
Explanation: In a sub-panel in a detached building, the neutral bus must be isolated from the panel enclosure and the equipment grounding bus. The equipment grounding conductor from the main panel should terminate on a separate grounding bus, which is bonded to the sub-panel enclosure. This prevents parallel neutral current paths on the grounding conductors and keeps the entire grounding system at the same potential.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.