A technician is troubleshooting nuisance tripping of a ground fault circuit interrupter (GFCI) protecting an outdoor receptacle. Using a clamp-on ammeter around the phase and neutral conductors feeding the GFCI, they measure 0.5 A flowing through phase and 0.45 A flowing through neutral. What is the MOST likely cause of the nuisance tripping?

A clamp-on ammeter reading of 0.5 A on phase and 0.45 A on neutral indicates a difference of 0.05 A (50 mA) between the two conductors. GFCIs typically trip at

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: A technician is troubleshooting nuisance tripping of a ground fault circuit interrupter (GFCI) protecting an outdoor receptacle. Using a clamp-on ammeter around the phase and neutral conductors feeding the GFCI, they measure 0.5 A flowing through phase and 0.45 A flowing through neutral. What is the MOST likely cause of the nuisance tripping?

Answer options: ✅ A small leakage current to ground downstream of the GFCI.

  • An overload condition on the protected circuit.
  • Voltage fluctuations on the incoming power supply.
  • A faulty GFCI receptacle that needs replacement.

Correct answer: A small leakage current to ground downstream of the GFCI.

Explanation: A clamp-on ammeter reading of 0.5 A on phase and 0.45 A on neutral indicates a difference of 0.05 A (50 mA) between the two conductors. GFCIs typically trip at 4-6mA of differential current. This difference suggests that current is leaving the phase conductor and returning to ground through an unintended path downstream of the GFCI, which is exactly what a GFCI is designed to detect and trip on. Overloads or voltage fluctuations do not typically cause this type of current imbalance.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.