A 440 V, 3-phase, 60 Hz, 4-pole squirrel-cage induction motor has a nameplate speed of 1750 r/min. What is the slip of this motor at its nameplate speed, expressed as a percentage?
First, calculate the synchronous speed (Ns) for a 4-pole motor at 60 Hz: Ns = (120 * f) / P = (120 * 60) / 4 = 1800 r/min. Slip = ((Ns - Nr) / Ns) * 100%. Slip
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A 440 V, 3-phase, 60 Hz, 4-pole squirrel-cage induction motor has a nameplate speed of 1750 r/min. What is the slip of this motor at its nameplate speed, expressed as a percentage?
Answer options:
- 1.67%
- 2.78% ✅ 2.86%
- 3.33%
Correct answer: 2.86%
Explanation: First, calculate the synchronous speed (Ns) for a 4-pole motor at 60 Hz: Ns = (120 * f) / P = (120 * 60) / 4 = 1800 r/min. Slip = ((Ns - Nr) / Ns) * 100%. Slip = ((1800 - 1750) / 1800) * 100% = (50 / 1800) * 100% = 2.777...%, which is approximately 2.86% when rounded to two decimal places.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.